MODULE 6 โ€” Frequency & Instrument Transformers

๐ŸŽต 6.1 Wien's Bridge โ€” Frequency Measurement

AC Bridge ยท f = 1/(2ฯ€RC) ยท Audio Range

Balance Condition

$$ \boxed{f = \frac{1}{2\pi\sqrt{R_1 R_3 C_1 C_3}}} $$
For $R_1=R_3=R,\;C_1=C_3=C$:
$$ \boxed{f = \frac{1}{2\pi RC}} $$

Arm Impedances

$$ Z_1 = R_1 + \frac{1}{j\omega C_1} \quad \text{(series)} $$
$$ Z_3 = \frac{R_3}{1 + j\omega C_3 R_3} \quad \text{(parallel)} $$

Ratio Arm Condition

$$ \frac{R_2}{R_4} = \frac{C_3}{C_1} + \frac{R_1}{R_3} $$
For equal R, C: $$ \boxed{\frac{R_2}{R_4} = 2} $$

Applications

Audio frequency measurement (20 Hz โ€“ 20 kHz)
Harmonic distortion analyzer
Accuracy: ยฑ0.1% to ยฑ1%
Notch filter / feedback oscillator
Rโ‚+Cโ‚ Rโ‚ƒโ€–Cโ‚ƒ Rโ‚‚ Rโ‚„ D AC Source f = โ€” Hz

๐ŸŽต Wien Bridge Frequency Calculator

f = โ€”

โšก 6.2 Instrument Transformers โ€” Overview

CT ยท PT ยท Isolation ยท Step-down

Current Transformer (CT)

$$ I_p \cdot N_p = I_s \cdot N_s $$
$$ \text{Nominal Ratio} = \frac{I_p}{I_s} = \frac{N_s}{N_p} $$
Secondary: 5A or 1A standard

Potential Transformer (PT)

$$ V_p \cdot N_s = V_s \cdot N_p $$
$$ \text{Nominal Ratio} = \frac{V_p}{V_s} = \frac{N_p}{N_s} $$
Secondary: 110V or 120V standard

Why Instrument Transformers?

$$ \text{1. Electrical isolation} $$
$$ \text{2. Extend instrument range} $$
$$ \text{3. Standardised meters} $$
Current Transformer
Ip Ns A
Potential Transformer
Np Ns V Vp

๐Ÿ“ 6.3 Transformer Ratios โ€” Nominal vs Actual

Ratio Correction Factor ยท RCF ยท Burden

CT Ratios

$$ K_n = \frac{I_p(\text{rated})}{I_s(\text{rated})} $$
$$ R = \frac{I_p(\text{actual})}{I_s(\text{actual})} $$
$$ \boxed{RCF = \frac{R}{K_n}} $$

PT Ratios

$$ K_n = \frac{V_p(\text{rated})}{V_s(\text{rated})} $$
$$ R = \frac{V_p(\text{actual})}{V_s(\text{actual})} $$
$$ \boxed{RCF = \frac{R}{K_n}} $$

True Value

$$ I_p = RCF \times K_n \times I_s $$
$$ V_p = RCF \times K_n \times V_s $$

Burden

CT Burden = Z_load on secondary (in VA or ฮฉ)
PT Burden = total VA of instruments on secondary
Higher burden โ†’ larger errors

๐Ÿ“ RCF Calculator

RCF = โ€” | Ip = โ€”

๐Ÿ”Œ 6.4 Current Transformer โ€” Complete Analysis

Ratio Error ยท Phase Error ยท Phasor Diagram

Ratio Error

$$ \boxed{\% \text{Ratio Error} = \frac{K_n I_s - I_p}{I_p} \times 100} $$

Phase Angle Error

$$ \boxed{\theta = \frac{180}{\pi}\cdot\frac{I_m \cos\delta - I_c \sin\delta}{n I_s}} $$
$I_m$ = magnetizing, $I_c$ = core loss component

Actual Ratio

$$ R = n + \frac{I_c \cos\delta + I_m \sin\delta}{I_s} $$
$n = N_s/N_p$, $\delta$ = secondary pf angle

Reducing CT Errors

Low core loss material (CRGO, Mumetal)
Large core cross-section โ†’ low B
Small secondary impedance (burden)
Turns compensation: add 1โ€“2 secondary turns
Ip nIs Iโ‚€ Im Ic ฮธ

๐Ÿ”Œ CT Error Calculator

% Ratio Error = โ€”

โšก 6.5 Potential Transformer โ€” Complete Analysis

Voltage Error ยท Phase Error ยท Capacitive PT

Voltage Ratio Error

$$ \boxed{\% \text{Ratio Error} = \frac{K_n V_s - V_p}{V_p} \times 100} $$

Phase Angle Error

$$ \boxed{\beta = \frac{180}{\pi}\cdot\frac{I_m R_s + I_c X_s}{K_n V_s}} $$
$R_s, X_s$ = secondary R & X referred to secondary

Actual Transformation Ratio

$$ R = K_n\!\left(1 + \frac{I_p(R_p\cos\phi+X_p\sin\phi)}{V_p}\right) $$

Reducing PT Errors

Low flux density in core
Small winding resistance & leakage
High permeability core (grain-oriented)
Capacitor voltage transformer (CVT) for EHV
Primary Rp Xp Ideal Kn:1 Secondary Rs' Xs' ZB Im+Ic Vp Vs

โšก PT Error Calculator

% Ratio Error = โ€”

โš ๏ธ 6.6 Errors in Instrument Transformers

Ratio Error ยท Phase Error ยท Burden Effect ยท Frequency

CT Ratio Error

$$ \varepsilon_R = \frac{K_n I_s - I_p}{I_p} \times 100\% $$
Positive โ†’ meter reads high

PT Ratio Error

$$ \varepsilon_V = \frac{K_n V_s - V_p}{V_p} \times 100\% $$
Depends on flux density & core loss

Factors Affecting Errors

$$ \text{Burden (VA)} \uparrow \Rightarrow \text{Error}\uparrow $$
$$ \text{Power Factor}\downarrow \Rightarrow \text{Phase Error}\uparrow $$
$$ \text{Frequency change} \Rightarrow \text{magnetizing error} $$

Accuracy Classes (IEC / IS)

ClassRatio Error (%)Phase Error (min)Application
0.1ยฑ0.1ยฑ5Precision lab
0.2ยฑ0.2ยฑ10Revenue metering
0.5ยฑ0.5ยฑ30Industrial metering
1.0ยฑ1.0ยฑ60General purpose
3.0ยฑ3.0โ€”Protection only

๐Ÿ“Š 6.7 Summary โ€” CT vs PT Comparison

Quick Reference ยท Key Differences ยท Safety
Parameter Current Transformer (CT) Potential Transformer (PT)
PurposeStep down currentStep down voltage
ConnectionSeries with lineParallel (across line)
PrimaryFew turns / bar (high I)Many turns (high V)
SecondaryMany turns โ†’ 5A / 1AFewer turns โ†’ 110V / 120V
BurdenLow Z (ammeter + wires)High Z (voltmeter)
Open CircuitDANGEROUS โ€” high voltage!Safe (no load)
Short CircuitSafe (normal condition)DANGEROUS โ€” high current!
Core operates atLow flux densityNear normal flux
Accuracy class0.1, 0.2, 0.5, 1.0, 3.00.1, 0.2, 0.5, 1.0, 3.0

โš ๏ธ Safety Rules

NEVER open-circuit a CT secondary under load!
NEVER short-circuit a PT secondary!
Always short CT secondary before removing ammeter
Ground one terminal of secondary winding