MODULE 7 β PT, CT vs PT & Power Measurement
πΆ 7.1 Potential Transformer β Complete Formulas
PT Ratio Β· Phase Angle Ξ² Β· Strip Wound CoreActual Transformation Ratio
$$ \boxed{R = n + \frac{I_m(R_s\cos\Delta + X_s\sin\Delta) + (I_c\cos\Delta - I_m\sin\Delta)r}{V_s}} $$
Simplified: $$ R \approx n + \frac{I_m\cos\delta + I_c\sin\delta}{nI_s \cdot V_s} $$
Phase Angle Ξ²
$$ \boxed{\beta = \frac{1}{nV_s}\left[X_s\cos\Delta - R_s\sin\Delta + \frac{I_m X_p - I_c r}{n}\right]} $$
$$ \beta_{deg} = \frac{180}{\pi}\cdot\beta_{rad} $$
Key Rules
$$ \text{CT: NEVER open secondary!} $$
$$ \text{PT: CAN be open-circuited} $$
Strip wound core β reduces ratio & phase error
Applications of CT & PT
Multiple operation with single device
Isolation from power circuit
Low power consumption
Easy replacement
πΆ PT Phase Angle Calculator
Ξ² = βΒ°
π 7.2 CT vs PT β Complete Comparison
Series vs Parallel Β· Flux Β· Danger RulesCT Formulas
$$ n_{CT} = \frac{N_s}{N_p},\quad k_n = \frac{I_{1,rated}}{I_{2,rated}} $$
$$ Z_{secondary} \approx 0\;\text{(short circuit)} $$
PT Formulas
$$ n_{PT} = \frac{N_p}{N_s},\quad k_n = \frac{V_{1,rated}}{V_{2,rated}} $$
$$ Z_{secondary} = \infty\;\text{(open circuit)} $$
Danger Rules
$$ \text{CT open} \Rightarrow V_s \to \infty \;\text{β οΈ} $$
$$ \text{PT short} \Rightarrow I_s \to \infty \;\text{β οΈ} $$
| Parameter | CT | PT |
|---|---|---|
| Purpose | High current measurement | High voltage measurement |
| Flux density & Iβ | Varies over WIDE range | Varies over RESTRICTED range |
| Secondary open circuit | NEVER β β οΈ DANGEROUS | CAN be open (safe) |
| Equivalent to | Series transformer (virtual short) | Parallel transformer (virtual open) |
| Primary current | INDEPENDENT of secondary | DEPENDENT on secondary burden |
| Primary terminal voltage | Small voltage across terminals | Full voltage across terminals |
CT β Series Connection
PT β Parallel Connection
β‘ 7.3 Measurement of Power β Overview
DC Β· 1-Ο AC Β· 3-Ο AC Β· Y & ΞDC Power
$$ P_{DC} = V_0 \cdot I_0 $$
1-Ο AC Power
$$ P = V_{rms}I_{rms}\cos\phi \;\text{(W)} $$
$$ Q = V_{rms}I_{rms}\sin\phi \;\text{(VAR)} $$
$$ \boxed{P = \frac{V_m I_m}{2}\cos\phi} $$
3-Ο AC Power
$$ P = \sqrt{3}\,V_L I_L\cos\phi $$
$$ Q = \sqrt{3}\,V_L I_L\sin\phi $$
Y-connection (Star)
$$ V_L = \sqrt{3}\,V_{ph},\quad I_L = I_{ph} $$
Ξ-connection (Delta)
$$ V_L = V_{ph},\quad I_L = \sqrt{3}\,I_{ph} $$
β‘ AC Power Calculator
P = β W | Q = β VAR | S = β VA
π 7.4 DC Power β V-A and A-V Methods
Error Analysis Β· R_critical Β· Method SelectionV-A Method
$$ P_m = P_t + I^2 R_A $$
$$ \boxed{\%\text{Error} = -\frac{R_A}{R_L}\times 100} $$
Best for: $R_L \gg R_A$ (high R load)
A-V Method
$$ P_m = P_t + \frac{V^2}{R_V} $$
$$ \boxed{\%\text{Error} = +\frac{R_L}{R_V}\times 100} $$
Best for: $R_L \ll R_V$ (low R load)
Crossover Point
$$ \boxed{R_{critical} = \sqrt{R_A \cdot R_V}} $$
$R_L > R_c$: V-A | $R_L < R_c$: A-V
| Parameter | V-A Method | A-V Method |
|---|---|---|
| Voltmeter position | Near supply (before A) | Near load (after A) |
| Extra power | $I^2 R_A$ (ammeter loss) | $V^2/R_V$ (voltmeter) |
| Error sign | Negative (overmeasures) | Positive (overmeasures) |
| Error formula | $-R_A/R_L \times 100\%$ | $+R_L/R_V \times 100\%$ |
| Best for | High R load ($R_L \gg R_A$) | Low R load ($R_L \ll R_V$) |
V-A Method
A-V Method
Recommended: β
π DC Power Error Calculator
V-A: β% | A-V: β% | R_crit = β
β‘ 7.5 AC Power β Two Wattmeter Method
3-Ο Power Β· Wβ+Wβ Β· tan Ο Β· cos ΟTwo Wattmeter Method
$$ \boxed{P_{total} = W_1 + W_2} $$
$$ \boxed{\tan\phi = \sqrt{3}\cdot\frac{W_1 - W_2}{W_1 + W_2}} $$
Individual Readings
$$ W_1 = V_L I_L\cos(30Β° - \phi) $$
$$ W_2 = V_L I_L\cos(30Β° + \phi) $$
Special Cases
$$ \phi = 0Β°:\; W_1 = W_2 \;\text{(pf=1)} $$
$$ \phi = 60Β°:\; W_2 = 0 \;\text{(pf=0.5)} $$
$$ \phi > 60Β°:\; W_2 < 0 \;\text{(reverse)} $$
Other Methods
One Wattmeter (balanced 3-Ο): P = 3Wβ
Three Wattmeter: P = Wβ + Wβ + Wβ
LPF Wattmeter: cos Ο < 0.5
pf = 0.866
Wβ > 0
β‘ Two Wattmeter Calculator
P = β W | tan Ο = β | cos Ο = β
π 7.6 Power Measurement β Summary
Quick Reference Β· All MethodsDC
$$ P = V_0 I_0 $$
V-A: $-R_A/R_L$
A-V: $+R_L/R_V$
1-Ο AC
$$ S^2 = P^2 + Q^2 $$
$$ P=VI\cos\phi,\;Q=VI\sin\phi $$
3-Ο
$$ P = \sqrt{3}V_LI_L\cos\phi $$
$$ \text{2W: } P = W_1+W_2 $$
| Circuit | Methods Available |
|---|---|
| DC | V-A method, A-V method |
| 1-Ο AC | V-A, A-V, EDM wattmeter |
| 3-Ο balanced | One wattmeter (Γ 3) |
| 3-Ο unbalanced | Three wattmeter method |
| 3-Ο (any) | Two wattmeter method |
π 3-Ο Power Calculator
P = β W | Q = β VAR | S = β VA